pole mounting and conduit questions [RE-wrenches]
Jeff Irish
jeff at hvce.com
Wed Jan 23 06:46:34 PST 2008
Talk to your AHJ. Ours let us slip the base plate and column over an 8 inch
high PVC stub out in the concrete base and run THWN-2 wire up the inside of
the column. Technically a 6 inch diameter steel pipe with 1/4 inch thick
walls is not a UL listed conduit but our AHJs believe adding an interior PVC
conduit would be silly and that the steel pipe provides more than adequate
protection. One however, requires us to run bare #6 down the outside of the
column.
Jeff Irish
Hudson Valley Clean Energy
-----Original Message-----
From: Nicholas Ponzio [mailto:nponzio at buildingenergyus.com]
Sent: Wednesday, January 23, 2008 9:33 AM
To: RE-wrenches at topica.com
Subject: pole mounting and conduit questions [RE-wrenches]
Does anyone have experience running conduit up through a pole? How do
you enter the pipe at the bottom? And do you run conduit all the way
up the pole or does the pole itself become your conduit?
We're using anchor bolts with a pre-welded plate on the bottom of the
steel pipe. See photo here:
http://www.flickr.com/photos/14918878@N04/2214585386/
What I'd like to do is run conduit up the inside of the pole and exit
through the "gimble" on the poletop. See an example of a light post
here: http://www.flickr.com/photos/14918878@N04/2214578212/
I haven't seen this done with PV but I'm sure it's possible. The DP&W
racks come with a knockout on the gimble, for this purpose. Not sure
about Zomeworks, though.
Any feedback is appreciated.
Thanks,
-Nik
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list