We are installing a PV system where an electrical contractor left us
an easy way to interface with the grid. The contractor does
extremely clean work which exceeds NEC requirements, and the local
code authorities are very happy with him.
What he left us was a 200 A, feed through breaker box that feeds no
branch circuits. The building that the breaker box is in is fed by a
separate, commercial service. The feeder on the feed through lugs,
from the box, goes to a residence where the wiring feeds a 200 A
service disconnect breaker for a residential electrical service.
The sole purpose of the breaker box is to give us a place for the PV
input. The potential code issue is that the PV input goes over the
20% limit. But there is no way the bus can be overloaded, since it
is protected by a 200 A breaker on the load side. Since the building
is commercial, and fed by a separate service, there would be no
reason to tap any loads from the box in question.
This doesn't look code compliant, from the wording of the NEC. Do
you think we should use the bus bar and backfeed a breaker, or tap in
ahead of the 200 A breaker to strictly meet code requirements.