Questions for Enphase Reps [RE-wrenches]

Mark Frye markf at berkeleysolar.com
Thu Jun 12 08:17:51 PDT 2008



Are there any representatives from Enphase on the list that can answer
questions about the new product?

I have so many questions about the product in general and how if conforms to
Code in specific:

Is the DC system grounded?

Clearly there are DC source circuits, the Code requires disconnects on
these. It makes some sense based on the architecture that they can do with
out them, but what about the Code which requires a disconnect on the DC
circuit?

The manual says:

"System Grounding
 Each Enphase Micro-Inverter has been provided with a ground clip that
can accommodate a 6-10 AWG conductor.
 Route a continuous Grounding Electrode Conductor through each of
the Micro-Inverters and AC branch circuit junction box to the NEC
approved AC grounding electrode."

This is somewhat misleading since the "DC system ground" must be a minimum
#8 per Article 250.

Could be the best thing since sliced bread

.
 
Mark Frye
Berkeley Solar Electric Systems
271 Vistamont Dr
Grass Valley CA 95945
(530) 401-8024
www.berkeleysolar.com 


[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list