Wrenches,

Last week we were discussing the "perfect" battery for grid tie with 
battery back up. I was mentioning a message from Windy about wet call 
lead calciums and found the message on the Topica archives. Here is a 
reposting of that message from 2001.

Todd


*Re: battery discussion* 	 Windy Dankoff, Dankoff Solar 
<http://lists.topica.com/lists/RE-wrenches/read/message.html?mid=1304009236&sort=d&start=4350#> 

 May 06, 2001 11:39 PDT 

Todd C wrote:

  	At the power plant I work at we have a bank of lead calcium cells. I
don't know much about these guy's chemistry. What experiences do list
members have with lead calcium batteries? What is they general best case
life and advantages over lead antimony.


Best advantages of lead calcium are to be experienced when you got
some in your hot little hands for next to nothing. They were a
mainstay of my business in late 70's and into 80's until AT&T got
sued over a public safety issue and had to protect us from their
"scrap". I know at least one customer still living on his 28-year old
set that he's had for 18 years.

THE trick to keeping them alive is to respect them as shallow cycle
batteries. Oversize the set for the application and cycle them no
more than 50%, except rarely. They have very low self-discharge, much
less than antimony, so extreme oversizing is not a problem in a
managed system. Also, they do NOT like high charge rates. When above
80% SOC, they overcharge at very low rates.

Use a hydrometer until you trust the accuracy of your amp-hour meter,
because their voltage is so stable, you can't get a SOC impression
from it.

Specific gravity is about 1100 discharged and only 1215 fully charged
(may vary according to the specific battery, that was true with
telephone exchange batteries). The low SG seems to correspond with
low energy density, so they are not for the space-challenged.

  	
Our bank is 15 years old now and last time we had to really cycle them
down (2 years ago), we did get their rated capacity, so I imagine they
are still doing ok. (I know it is bad to take batteries below 50 to 70%
DOD.) I am curious how other than capacity testing one determines
current health and remaining life span?


Are they clear-case cells? If so, you can see if sediment is
substantial. Little sparkles are a good sign on the neg plates, but
not assurance of good. White powder is usually a sign that they are
ready for rebirth.

  	
The bank is 10, 12 volt batteries, so ~120 VDC. Their self discharge
rate is s-l-o-w-l-y increasing. They are being kept at around 70=BA F. The
charge voltage set point at 135 volts. Any higher and the inverter kicks
off from over voltage, so it is hard to do an equalization charge and at
present they do not consume any water at all. I am thinking about
removing one battery (6 volts) to lower the pack voltage so I can
effectively raise the per cell charge voltage (without upsetting the
inverter) to attempt to keep them a bit happier. Any comments on this
plan?


I think I remember that EQ overcharging is not advised for calcium
batteries, unless they have problems showing up.

I would get a V reading AND a S.G. reading of every cell. If they are
really even (within 5 points SG), you probably have a very good set
that can last a lot more years.

There are many sources of batteries like this. They are usually
cycled out per schedule, long before their useful life is over, by
nature of the applications where they must be trusted for
emergencies. I used them to run my shop and home in the 80's. The
ones I used are now part of an old customer's set and still working.
Don't forget to add water every few years!

Windy


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------

</x-flowed>



More information about the RE-wrenches mailing list