Flex ware inverter bypass slide [RE-wrenches]
Todd Cory, Mt. Shasta Energy Services
toddcory at finestplanet.com
Thu Nov 29 17:16:25 PST 2007
<x-flowed>
To the left of the two, double pole circuit breakers on the Midnight
e-panel's bypass switch is a two pole, 30 amp generator input breaker.
There is no need to walk to the generator to disconnect it's output
power when the inverter input breaker is right there on the e-panel.
Todd
Christopher Freitas --- OutBack Power wrote:
>So you are saying that its OK that the operator has to walk all the way
>out to where the generator is to shut off its circuit breaker in order
>to disconnect all sources of power from the loads?
>
>And you think this is acceptable and code compliant? Come on now...
>
>Christopher
>
>
>Todd Cory wrote:
>
>
>>With the generator input breaker off, switching to bypass shuts
>>everything off since you are bypassing to a de-energized circuit.
>>
>>Todd
>>
- - - -