Flex ware inverter bypass slide [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Thu Nov 29 17:15:10 PST 2007
OK - lets take the gloves off...
Sure the Midnite box cost less - it only works with one inverter - not
two! It also holds much fewer breakers and other components - such as
multiple shunts.
The door mounted inverter is the worst idea in my opinion - you can't
even open the door up much past 45 degrees with the cable provided - and
they put a lot of stress on the terminals of the breaker - which can
result in a loose connection that you don't even notice when the door is
open - which then causes a fire...
There are requirements for the routing of wires out to a door mounted
component which are not met by the Midnite "E" panel. Things like
strain relief loops and tie downs straps and dedicated space for the
wires to lay by the hinge - none of this is done in the E-panel.
Proper construction also usually involves a protective loom over the
wires to keep them from being damaged by sharp edges of other parts
inside (like the shunt) or being pinched and having the insulation on
the wires be damaged.
Another issue with the E-panel is that there is no ground wire provided
for the inverter chassis - this means that when the door is open the
chassis of the inverter is not grounded (the tabs they think are a hinge
do not provide any means of grounding) so if there was a ground fault in
the inverter itself the whole door could become electrified when you
open it - that's a really nice surprise...
The requirements in UL and NEC standards are there for a reason - to
protect you guys!
I think the inverter on the door idea is dangerous and just a bad idea
all round.
Any other opinions or comments?
Christopher
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list