Xantrex XW [RE-wrenches]
Ray Walters
walters at taosnet.com
Tue Nov 6 07:16:10 PST 2007
<x-flowed>
We had just this problem with GFP in an old system. There was a
ground fault in the 12 v DC lighting in the house that caused the PV
array GFP to trip. They do indeed see the entire system, which is
annoying sometimes.
Ray
Solarray.com
On Nov 6, 2007, at 7:43 AM, John Raynes wrote:
>
> What would happen in a system with more than one XW charge
> controller tied into the same DC bus? Wouldn't each controller see
> the other's GFP as an external ground fault? I would hope that
> there would be some way of disabling the internal GFP in lieu of a
> single system GFP breaker, external to the CCs.
>
> John Raynes
> RE Solar
> Torrey, UT
>
>
> At 07:36 PM 11/5/2007 -0700, you wrote:
>
>> Ken,
>>
>> From what I've seen, the XW charge controller has GFP built in to
>> it, so if
>> you're using that controller, negative and ground must be kept
>> isolated so
>> the GFP will work correctly, and probably for the controller to
>> work at all.
>> If you're using a different charge controller, you'll be OK unless
>> you want
>> GFP, in which case you may need to install a Midnite baby box and
>> Midnite
>> GFP(s) and separate negative from ground, or some other kluge (and
>> I mean
>> that in a GOOD way). As far as I can tell, a solid neutral-ground
>> bond does
>> not adversely affect the inverter in any way.
>>
>> The fact that Xantrex chose to use a GFP fuse inside the
>> controller (and an
>> expensive 600 VDC KLKD fuse at that) instead of a separate breaker
>> is a poor
>> call IMO. A ground fault anywhere in the system, not just in the
>> array
>> wiring, will cost you the price of that fuse. Not sure what
>> Xantrex has
>> planned for GFP in the new distribution panel when using somebody
>> else's
>> charge controller either. Maybe ye olde Trace PVGFP from years
>> back will
>> mount up to the DC breaker panel in the new enclosure, since it
>> uses the
>> correct size breakers. It appears to still be available (that is,
>> the manual
>> is not in the "discontinued products documents" list).
>>
>> Looking forward to hearing your thoughts on the inverter.
>>
>> Dan Rice
>> Abundant Sun, LLC.
>>
>> ----- Original Message -----
>> From: "Ken Schaal" <ken at commonwealthsolar.com>
>> To: <RE-wrenches at topica.com>
>> Sent: Monday, November 05, 2007 4:56 AM
>> Subject: Re: Xantrex XW [RE-wrenches]
>>
>>
>> |
>> | As I mentioned in my last post, we are doing a Y2K system
>> upgrade so we
>> can
>> | net meter and have gen backup, at affordable prices.
>> | The 6048 XW is now on the wall and wired into the existing Trace DC
>> | disconnect and transfer switches. After wrestling the old Power
>> Panel down
>> | off the wall---I use two 'farm jacks' for that joyful task---,
>> it was a
>> | pleasure to bolt a bracket to the wall and lift the 125# XW into
>> a slot on
>> | the bracket that carries the weight and then secure in the vertical
>> position
>> | with two screws at the top.
>> | Sweet!
>> | We will be finishing the install today I trust and start to play
>> with it,
>> | although the net meter inspection and appropriate meter install
>> is still
>> in
>> | progress.
>> | Our only hassle so far is due to our use of the existing DC
>> disconnect,
>> and
>> | the fact that we will be adding an additional array,
>> necessitating a
>> second
>> | charge control, both mounted above the Trace disconnect where
>> the original
>> | C40's were mounted. The knockouts don't quite align, so we had
>> to do a
>> | little grinding, about 3/8 ".
>> | The other thing we noticed is that the old Trace disconnect has
>> common
>> | battery neg and equipment ground, where the new XW disconnect uses
>> seperate
>> | buses, with the battery neg isolated. Any thoughts on how big an
>> issue
>> this
>> | is?
>> | The new XW distribution panel is quite complete with transfer
>> breakers,
>> nice
>> | flex wire, etc but does cost $1K, so the temptation for many
>> will be to
>> use
>> | the existing Trace.
>> |
>> | More thoughts to follow after we try it out with the existing
>> array.
>> |
>> | Ken Schaal
>> | CommonWealth Solar
>> |
>> | ----- Original Message -----
>> | From: <i2p at aol.com>
>> | To: <RE-wrenches at topica.com>
>> | Sent: Sunday, November 04, 2007 3:15 PM
>> | Subject: Re: Xantrex XW [RE-wrenches]
>> |
>> |
>> | >
>> | >
>> | >
>> | > In a message dated 11/3/2007 6:34:33 A.M. Pacific Standard Time,
>> | > jay at asis.com writes:
>> | >
>> | > What are the comments about the new XW equipment.
>> | >
>> | >
>> | >
>> | > Me too, waiting.
>> | >
>> | > Don L
>> | >
>> | >
>>
>>
>> - - - -
>> Hosted by Home Power magazine
>>
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages: http://lists.topica.com/lists/RE-
>> wrenches/read
>>
>> List rules & how to change your email address: www.mrsharkey.com/
>> wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Moderator: michael.welch at homepower.com
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list