equipment grounding conductors [RE-wrenches]
Drake Chamberlin
Drake.Chamberlin at redwoodalliance.org
Wed Oct 24 07:10:28 PDT 2007
Correction:
We size the wire for 125% short circuit current.
Drake
Drake Chamberlin wrote:
>
> Hello Wrenches,
>
> NEC 250.118 lists equipment grounding conductor types. EMT is one type
> of equipment grounding conductor that is listed.
>
> To be on the safe side, we usually run a wire in EMT, from the solar
> array, that is rated at 125% of full load current per 690 requirements.
>
>
>
> The NEC Handbook gives some idea concerning what size that rigid metal
> conduits are permitted for equipment grounding, for various amperages in
>
> feeders, although the NEC itself doesn't.
>
> In the past, I used EMT conduit to ground runs from solar arrays, the
> same way that I use the pipe to ground other circuits. Can we still use
>
> it? What are the guidelines for determining what amperage or wire size
> is allowed to be grounded in this way.
>
> Thanks,
>
> Drake
- - - -