equipment grounding conductors [RE-wrenches]

Drake Chamberlin Drake.Chamberlin at redwoodalliance.org
Wed Oct 24 07:10:28 PDT 2007


Correction:

We size the wire for 125% short circuit current.

Drake 


Drake Chamberlin wrote:
> 
> Hello Wrenches, 
> 
> NEC 250.118 lists equipment grounding conductor types.  EMT is one type 
> of equipment grounding conductor that is listed.  
> 
> To be on the safe side, we usually run a wire in EMT, from the solar 
> array, that is rated at 125% of full load current per 690 requirements.  
> 
> 
> 
> The NEC Handbook gives some idea concerning what size that rigid metal 
> conduits are permitted for equipment grounding, for various amperages in 
> 
> feeders, although the NEC itself doesn't.  
> 
> In the past, I used EMT conduit to ground runs from solar arrays, the 
> same way that I use the pipe to ground other circuits.  Can we still use 
> 
> it?  What are the guidelines for determining what amperage or wire size 
> is allowed to be grounded in this way. 
> 
> Thanks,
> 
> Drake 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-wrenches mailing list