Outback and gensets was: Selecting an inverter/battery system [RE-wr [RE-wre
Steve Johnson
stevejohnson at comcast.net
Tue Sep 11 19:24:40 PDT 2007
Interesting thread. Sounds like the generator support issue isn't a
problem if the generator can handle the AC loads plus battery charging
at the same time.
The European Sunny Islands can be ordered at 60Hz and will support a
multi cluster of 12 units at 3 phase. However it is European 3 phase
which is 230/400Y. That would have to be transformed to whatever your
mini-grid is. Of course this would be for use out of the US.
Sunny Boys are also available at 230v 3 phase if they were to be AC
coupled to the Sunny Islands.
Steve Johnson
LightWave Solar Electric
Nashville, Tennessee
wratterman at SunEnergyPower.com wrote:
>
> Jeff:
>
> Walt Ratterman here.
>
> I have done many Outback hybrid systems with generators and all of them
> are in very remote areas. I would be glad to share with you what I have
> learned.
>
> I am in route back to the states now, and if you want we can discuss
> these issues over the phone, but some basic principles are:
>
> The generators should not be undersized.
>
> If you are using large, three phase generators, you should see if it
> works to make the Outback system three phase as well - balances out the
> charging load on the generator much better, and works well.
>
> Be sure not to get a cheap generator, or a "standby" generator.
>
> I simply refuse to do any automatic start systems anymore. Even if the
> generator controls are great, and everything seems like it will work, I
> will not do it. These remote systems need to have operators who are
> interested and know that the systems require constant attention.
>
> Instead of auto-start, I use the aux relay to (a) light a light in a
> prominent location to indicate that the system thinks the batteries need
> charging soon, and (b) sound a loud, obnoxious horn. I have it so the
> horn can be silenced for 6 hours, but the light can will not go out
> until the system is no longer calling for a charge.
>
> I set all of the battery protection set points considerably higher (more
> conservative) than the factory defaults.
>
> And then......lots and lots and lots of training.
>
> Be glad to go over more with you off line. Just did a bunch of
> hospitals - some solar some shitty grid UPS systems, all over Rwanda....
>
> See ya,
>
> Walt
>
> -----Original Message-----
> From: Jeff Oldham [mailto:starpower4u at juno.com]
> Sent: Tuesday, September 04, 2007 1:05 PM
> To: RE-wrenches at topica.com
> Subject: Outback and gensets was: Selecting an inverter/battery system
> [RE-wrenches] [R
>
>
>
> I'm about to embark on two very large o-t-g genset/inverter projects,
> one w/28 inverters and a modest 16kW PV array and the other w/10
> inverters and no PV for now. These both need to rely on genset interface
> and I have not got a handle on the Outback genset interface issues that
> some have spoke of. Please enlighten me before I get in too deep, these
> are both outside of the U.S. and very remote so any "small" issue is
> really a very big issue. I've yet to experience any issues so far
> w/Outback and gensets but I tend to not do many fully automated systems
> w/auto start/stop and perfer the human interaction and logic.
> Much thanks!
> -jeff o.
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list