WIRE CALCS [RE-wrenches]
Ray Walters
walters at taosnet.com
Mon Jul 16 12:46:55 PDT 2007
<x-flowed>
We too have an excel sizer that you can also do cost comparisons with
(energy lost vs. wire cost).
IT has temp derating settings based right off the NEC tables.
Let me know what you think, its a work in progress.
Its at on the right side bottom of the page:
http://www.solarray.com/TechGuides/TGmain_T.php
Ray Walters
On Jul 16, 2007, at 8:07 AM, Dana Orzel wrote:
>
> Wire and Conduit sizing
>
> We use the Electricalc calculator, made by Calculated Industries,
> Carson
> City, NV - Tel # - 702.885.4975. You can specify the watts, volts,
> amps,
> volt drop in volts and or volt drop %, length of run - distance,
> wire size,
> type of conductors, number of conductors, multiple conductors of
> varying
> sizes, size conduit, size ground conductor, ands about 30 other
> items I have
> never had use for.
>
> This is unit specific to the latest code and you can now get it
> with the
> capability to upgrade to the latest version of the code without
> replacing
> the entire calculator, you just replace the chip. I do not leave
> the office
> without it, as it is great for in field calculations.
>
> Great Solar works, Inc.
> www.solarwork.com
> t - 970.626.5253
> f - 970.626.4140
> c - 970.206.4076
>
>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list