WIRE CALCS [RE-wrenches]
Hugh Piggott
hugh at scoraigwind.co.uk
Mon Jul 16 09:44:41 PDT 2007
<x-flowed>
The nice thing about metric wire sizes is that you can calculate the
volt drop in your head most of the time. Or at least near enough,
given that it depends pretty heavily on temperature anyway.
At around ambient temperature a 2-way 1 sqmm cable has resistance 1
ohm for each 28 metres. I often use 30 metres in rough calcs. For
example 100 metres wire run (one way) 10 sqmm would have total
resistance (both wires) 0.36 ohms. If you are pumping 4 amps down it
then the volt drop will be 1.4 volts.
There must be a similar trick with AWG, given that it does follow a
crazy logarithmic logic (doubling with every 3 wires sizes).
--
Hugh Piggott
Scoraig Wind Electric
http://www.scoraigwind.co.uk
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list