Combining SQFlex PV direct with grid tie [RE-wrenches]
Kurt Albershardt
info at es-ee.com
Mon Jun 18 15:03:36 PDT 2007
<x-flowed>
Thanks -- that looks like it might be the least complicated way to achieve the desired result.
>From p.20 of the product guide:
The IO 101 enables the connection of a generator
supply back-up in case of insufficient solar radiation.
The switching between solar power and generator must
be made manually.
When the generator is stopped manually or runs out of
fuel, the IO 101 will automatically switch to the solar
energy supply.
So they *almost* built what I had planned...
--On Monday, June 18, 2007 9:46 PM +0000 Brad Bassett <bbassett at hei.net> wrote:
>
> Kurt,
>
> You can use the Grundfos I/O 101 in the pump circuit and when grid is up
> the pv will feed the grid tie inverter and the pump will run on AC. When
> the grid it down the I/O 101 will automatically switch the pump to the
> pv. The trick is getting the voltages in range for both. The lower range
> for the SMA 1100 will work but that is a discontinued model, some around
> still. The 700 will work but will limit which modules you can use, and
> the 2kW range inverters will make it harder to keep the voltage low
> enough. The max on the SQFlex is 300vDC and you should take into
> account the voltage rise at low temps. Also keep in mind that the I/O
> 101 is only good for 120vAC, not 240.
>
> Thanks,
> Brad Bassett
> AEE
.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list