balancing a 3-phase panel? [RE-wrenches]
Steve Johnson
stevejohnson at comcast.net
Sun Jun 10 18:06:59 PDT 2007
Geoff,
On new buildings, in the specifications under Div. 16, the electrical
engineer will sometimes call for 3 phase legs to be balanced within __%.
I think it is 5 % but I'm not sure. This is refering to the loads of
course, but it is the same principle. Acutally the PV is a negative
load from that point of view. Since loads are always changing it is
just a general guideline.
If you put an amprobe on the 400 amp main and found Phase A to be 10%
higher than Phases B and C and you hooked up to Phase B and C with 15%
input of PV then the resulting 25% variance may be off some concern.
You would want to hook up to AB or AC to level things out a bit.
I havnen't found it to be a problem so far on 600 amp services with
12kw. The 2 6kw inverters were combined in a panel so that only 1 phase
overlapped when it was fed into the system.
Steve Johnson
LightWave Solar Electric
Nashville, Tennessee
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list