Mark,

My understanding is that it is not allowed to exceed the 360 rule. All that
you need is a pull box or some other means for pulling conductors. I believe
an LB or condulet would comply just fine. 

Bill.

Bill Brooks, PE
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
office and mobile phone: 707-332-0761
fax:707-451-7739
email: billbrooks7 at yahoo.com
web: www.brooksolar.com

Ecclesiastes 11:7 Light is sweet, and it pleases the eyes to see the sun.


> -----Original Message-----
> From: Mark Frye [mailto:markf at berkeleysolar.com]
> Sent: Wednesday, May 16, 2007 8:03 PM
> To: RE-wrenches
> Subject: Flexible Conduit [RE-wrenches]
> 
> 
> If I pre-load conductors into a flexible conduit while it's striaght,
> prior
> to pulling it thought the framing, can I exceed 360 degrees of bending
> once
> it is in place?
> 
> MPF


- - - -