Breaker space in PS-2DC [RE-wrenches]
Allan Sindelar
allan at positiveenergysolar.com
Tue Apr 24 14:34:55 PDT 2007
Geoff,
1. Add a Midnite MNPV-3 or -6 for additional breaker space.
2. Can you replace GF inverter breakers (175 or 250A) with smaller CD
breakers (100 or 125A)? That would free up a bit of space.
3. Combine the outputs on a single breaker, with individual supplemental
fuses on each controller.
Allan at PosE
----- Original Message -----
From: "Geoff Greenfield" <Geoff at Third-Sun.Com>
To: <RE-wrenches at topica.com>
Sent: Tuesday, April 24, 2007 12:48 PM
Subject: Breaker space in PS-2DC [RE-wrenches]
>
> I have a customer with a PS-2DC with 2 inverters and 2 MX-60s... He would
> like to expand his array (adding a 3rd MX-60). The problem is we have
only
> 3 breaker spaces left and I figure I need 3 for a second GFI and a fourth
> for the DC disco to the MX-60.
>
> The mx-60 could be current limited to 43 amps - what would you all say to
> using the gfi on both sides (prob no good as I think the gfi is not a
> current limiting device). Maybe I could add a DC fuse inside to handle
that
> and just use the gfi as disconnect means.
>
> Other work around would be a kluged add on box to hold a DC breaker (or
> GFI). Not clean, but do-able.
>
> This is rural and not inspected but our policy is to work safely and to
the
> NEC (or to it's intent when we are the design review).
>
> Any suggestions would be appreciated!
>
> For a brighter energy future,
>
> Geoff Greenfield
> President
> Third Sun Solar & Wind Power Ltd.
> 340 West State street, Unit 25
> Athens, Ohio 45701
> (740) 597-3111 fax: (740)597-1548
> www.third-sun.com
>
> Clean Energy - Expertly Installed
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
>
> --
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.463 / Virus Database: 269.5.10/774 - Release Date: 4/23/2007
5:26 PM
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list