Converting Off-Grid OB to Grid-Tie [RE-wrenches]

Todd Cory, Mt. Shasta Energy Services toddcory at finestplanet.com
Fri Feb 23 08:30:22 PST 2007


<x-flowed>

If you send the inverter back into Outback, they will swap out the board 
and test it for compliance, which will change it from a VFX to a GVFX. 
If you do not need two inverters, just convert the existing one.

Todd

David Palumbo, Independent Power & Light wrote:

>
>All,
>
>I have a customer who is converting his off-grid Out Back system to a
>grid-tied system. He asks the following:
>
><<- I know Outback sells the GTFX2524 and GTFX3524; obviously we'll need to
>see which one is appropriate to the system upon redesign, but I am
>wondering if there is a way to still incorporate the existing 2024 to
>charge off the panels, and run the GTFX2524 along side, or if this is
>foolish and overcomplicated, and I should look towards selling the 2024
>(or keeping it as emergency back-up?).>>
>
>Anyway to incorporate his four yr old FX 2024 into a GTFX system?
>
>Thanks for your time,
>Dave
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>



More information about the RE-wrenches mailing list