starting a 1 HP well pump with a VFX3648 [RE-wrenches]
Drake Chamberlin
Drake.Chamberlin at redwoodalliance.org
Fri Jan 26 20:01:10 PST 2007
<x-flowed>
At 02:21 PM 1/26/2007, you wrote:
>9 Table 8 and find the wire
>size--ohms/1000 feet and calculate the volt drop VD= I
>x ohms/kft x (total ft round trip)/1000, This should
>not bemore than 3 or 5%
The resistance isn't quite as bad as table 8 makes it look, since the
resistance in the table is for wire at 75 degrees C, or 168 degrees
F. There is a formula at the bottom of the chart for converting to
the temperature that the wire will be operating at. Since the wire
is underground for part of its run, and then underwater for remainder
of its run, it should be safe to use 70 degrees F.
On the other hand, the pump is a reactive load, which complicates
things a bit further. Table 9 has AC reactance values, but these are
for 3 phase circuits.
Don't the pump specifications give information on wire size for
distance directly, or do they make the installer calculate it?
Drake
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list