GT series inverter certification [RE-wrenches]
Joe Felker
joe.felker at alumni.stevens-tech.edu
Fri Jan 19 10:09:16 PST 2007
Go to the wire manufacturer and get their spec sheet that states the
cable is Sunlight Resistant. I was able to do this to satisfy a local
inspector
Mark Frye wrote:
>
> Thanks Allan,
>
> John's Code Corner #66 addresses this issue. I have sent a copy to the
> AHJ,
> but he states that he cannot "rely" on the article. At least he has it
> so
> he can get up to speed if he wants to.
>
> I had to send him a copy of the spec sheet that shows that the wire is
> listed to UL 854. UL 854 is the spec for Service Entrance conductors
> where
> it is specified that the wire is not marked "sunlight resistant" but has
> been tested for the same.
>
> Mark Frye
> Berkeley Solar Electric Systems
> 2504 Webster St
> Berkeley CA 94705-2504
> (510) 685-3042
> markf at berkeleysolar.com
> www.berkeleysolar.com
>
>
> -----Original Message-----
> From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
> Sent: Friday, January 19, 2007 6:51 AM
> To: RE-wrenches at topica.com
> Subject: Re: GT series inverter certification [RE-wrenches]
>
>
>
> Mark,
> This is from my memory of a recent John Wiles PV/Code seminar, so I may
> be
> incorrect here: USE-2 is sunlight-resistant whether marked or not.
>
> You might contact John directly for assistance with this issue. 505
> 646-6105, or jwiles at nmsu.edu.
>
> Allan at Positive Energy
>
> ----- Original Message -----
> >Today I had a City
> > of Berkeley inspector reject my installation because the USE-2 cable was
> not
> > marked "sunlight resistant".
> >
> > Mark Frye
> > Berkeley Solar Electric Systems
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
Joe Felker
Engineering Manager
NABCEP Certified Solar PV Installer
The Solar Center
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list