GFP on SDHW pv pump? [RE-wrenches]
Brad Bassett
bbassett at hei.net
Fri Nov 16 10:10:28 PST 2007
Jay,
He tried unsuccessfully to argue low voltage. I don't see any exceptions
under 690.5 in the 2002 or 2005 codes.
John R.,
A referral to John Wiles might help in this instance?
Thanks,
Brad
jay peltz wrote:
>
> HI Brad,
>
> Would it fall under the low voltage section?
>
> Or how about using a "pole". 690.5 exception 1.
>
> jay
>
> peltz power
> On Nov 16, 2007, at 9:41 AM, Brad Bassett wrote:
>
> >
> > I have a customer installing SDHW systems with PV powered pumps and
> > the
> > inspector is now saying they have to use a GFP on this 10w module when
> > installed on a dwelling! If this continues and they adopt the 2008
> > code
> > it would have to be done for all installations. I can't find any
> > exceptions in the code to fight this (one would think common sense
> > would
> > work). As I see it one of the breaker based GFP's is about the only
> > choice and at 0.5A trip point a dead short in a 10W module would only
> > occasionally even trip it. Any ideas?
> >
> > Brad Bassett
> > AEE Solar
> >
> >
>
Brad Bassett
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list