Sanyo HIT panels in off grid app [RE-wrenches]
Ron Young
solareagle at solareagle.com
Sat Nov 3 11:34:50 PDT 2007
<x-flowed>
Thanks Jay, I kept hitting .7 on the calculation instead of .17 &
Mick, I'll check out the XW sizing chart, thx. I'll still have to
whack my fingers with a wrench if they keep inputting the wrong data ...
On 3-Nov-07, at 7:32 AM, Jay Peltz, Peltz Power wrote:
>
> Hi ron,
>
> Maybe my calculator is wrong but 39 x .170= 6.63
>
> So 2 modules in series = 13.26v
> + 68v x 2 = 136
> +13.26
> = 149v
>
> On the edge but there.
> jay
>
> peltz power
> On Nov 3, 2007, at 1:00 AM, Ron Young wrote:
>
>>
>> Okay so here's where I'm getting mired down. The Sanyo 195 has a
>> Voc of 68.1. I'm using a temp correction factor of .170 per degree
>> C (ref. the chart in Home Power #121) and potential low temps
>> around -14 degrees C. in my locale. Based on the 25 degree STC
>> ref. temp that works out to 39 x .170 = 27.3 volt correction
>> factor. This results in an effective Voc of 68.1 + 27.3 = 95.4
>> which seems unreasonable to me, have I miscalculated? Is the temp
>> correction factor only relevant for NEC compliance which doesn't
>> apply in my off-grid situation?
>>
>> Earlier in this discussion I was using a temp. correction factor
>> of 1.25 which gave me Voc of 68.1 x 1.25 = 85.12.
>>
>> In either case a series connection of two modules will be
>> impossible with an MX60, exceeding the maximum output voltage of ~
>> 140 V.
>>
>> Ron Young
>> earthRight Solar
>>
>>
>>> From: Ryan Mayfield <ryan_mayfield at earthlink.net>
>>>
>>>
>>> There is a great PV reference chart in the last Home Power, #121.
>>> From
>>> that info, the Sanyo 190 has a Voc temperature correction factor of
>>> -0.169V per degree C.
>>>
>>> Ryan
>>
>> On 2-Nov-07, at 9:15 AM, Jay Peltz, Peltz Power wrote:
>>
>>>
>>> Hi Larry,
>>>
>>> The 190s are 67.5v, so x 2 = 135VOC
>>> which give around 15v to play with.
>>>
>>> I don't have their voltage adjustment figures in front of me, but
>>> when I did the calculations given our
>>> record lows, it was close but the numbers did work out OK for the
>>> 2 in series.
>>>
>>> jay
>>>
>>> peltz power
>>>
>>
>>
>>> From: William Miller <wrmiller at charter.net>
>>>
>>> Ron:
>>>
>>> When calculating total Voc there are two considerations: legal
>>> and technical.
>>>
>>> The NEC compliance has only come into relevance for my projects
>>> when the total VOC as corrected by NEC correction factors exceeds
>>> 600 VDC.
>>>
>>> In this case, the only limit is the manufacturer's design
>>> limitations in the charge controller. Using NEC correction
>>> factors is irrelevant here. Instead, the module manufacturer's
>>> or the industries correction factors must be applied. I don't
>>> use them often and don't have them handy, but I am certain
>>> someone else on the lists does.
>>>
>>> William Miller
>>>
>>>
>>
>>
>> - - - -
>> Hosted by Home Power magazine
>>
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages: http://lists.topica.com/lists/RE-
>> wrenches/read
>>
>> List rules & how to change your email address: www.mrsharkey.com/
>> wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Moderator: michael.welch at homepower.com
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list