Sanyo HIT panels in off grid app [RE-wrenches]
Mick Abraham
mick at abrahamsolar.com
Sat Nov 3 02:31:19 PDT 2007
Ron Young wrote about getting "mired down" with the voltage
calculations, temperature factors, etc., when doing string sizing for a
battery charging type controller.
Mick says: The Xantrex XW charge controller accepts a maximum open
circuit input voltage of 150, versus 140 for the Outback MX. There's a
nice temperature compensated string sizing tool at the XW website which
does all the code related math for you. Look under the Downloads column
to find this. The sizing tool works much the same as the tools for
string sizing with Fronius or other grid tie inverters.
The XW sizing tool allows for two Sanyo 200's in series only if the
record low temperature is 12 degrees F or higher. This is because of all
the code derations and fudge factors which an alert code inspector might
impose. If the system is not being inspected with close attention to
detail, common sense might also come into play.
Mick Abraham, Proprietor
www.abrahamsolar.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list