Battery enclosures and NEC [RE-wrenches]
John Raynes
john at raynes.com
Thu Oct 4 11:51:59 PDT 2007
<x-flowed>
Thanks all for the great feedback to my earlier questions.
One additional question I have about "site-built" fiberglass or HDPE
liners fabricated from sheet stock: By definition, there are gaps
between the bottom deck and the side lips. What's the best
acid-resistant caulk material to use to seal those interfaces?
We've looked at the pre-fab spill containment trays from time to time,
our problem is that it costs at least as much and perhaps even more to
ship than the item itself costs, and there's so many variations on
battery sizes, orientations, etc. That same rule about buying pre-fab
also applies to battery boxes unless they can be broken down for
shipping. We're 10 hours drive from the nearest full line solar
distributor, 3 hours from the nearest freight depot so we rarely pick
up anything ourselves, and all freight is interlined.
I hear Jeff's comments about moving to commercially built boxes
someday, but they add significant expense, even without the shipping
costs. I would hope for a compromise solution where construction
techniques and materials are more fully specified for all important
details, such as acid resistance, flame retardancy, strength, back
draft protection, no access without a tool, etc.
We build our enclosures out of 3/4 plywood for the deck, 1/2 OSB sides
and top, with 1-1/2 to 2 inches of foam all around. We rip framing
lumber into appropriate sizes for strength and fastening support on all
edges. I try to avoid site built wherever possible, so I have a basic
design that breaks down into 6 or 7 flat pieces for transport to site.
If I can pre-build at the shop things always turns out better. That
pretty much applies to everything we do.
John Raynes
RE Solar
Torrey UT
At 10:37 AM 10/4/2007 -0700, you wrote:
We started out building tight battery boxes for all our projects which
included a lock hasp on the cover door, but finally switched over to
battery "rooms".
We now work with the builder or architect on new construction to
include a long and narrow room dedicated for only the batteries, with
the inverter on a the outside wall surface for this room. The room is
constructed of heavier fire-rated green-board drywall on the interior
walls and ceiling, a concrete floor with floor drain, and a DC in line
exhaust fan located at the highest point and powered from the inverter.
We also add a fire extinguisher and safety signage on the access door
which is locked.
When we switched away from battery boxes, all our past battery and
battery cable corrosion problems dis-appeared. The tight battery boxes
were providing an very acid-rich environment that would destroy battery
cables in less than 3 years, not to mention the piles of corrosion we
had to clean off each year. Now when I check on an older battery room
system, you could eat off the floor and the battery terminals are as
clean as they day they were installed.
I think the days of site-built battery boxes are numbered, most likely
when the NEC takes a look at the safety issues of many poorly
constructed site built boxes that are out there now. It would not
surprise me if battery boxes will someday need to be commercially made
and tested to some kind of UL listing that addresses proper venting,
door safety, drains, door seals, fire-rated materials, explosive
containment, and include a certification label on the cover. Just my 2
cents.....
Jeff Yago, NABCEP Certified DTI Solar
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list