Allen,
Grundfos says that they are not to be used where GFI protection is
required. I did have one customer try it for a pool fountain (one of the
for sure places where a GFI is required) and the pump always tripped the
GFI.
As for the control problem, it is probably in the motor. The CU200 only
reports what the motor is telling it. Even the on/off switch is only a
command to the motor to stop. So the wires to the pump are still live
when the switch is off! But, first make sure that the terminal block
that the pump wires are connected to in the CU200 is solidly seated on
the circuit board. This often comes loose if the wires pull on it and
can make for an intermittent connection.
Brad Bassett
AEE Solar
> Brad Bassett of AEE has reported that the pump won't work through
> a
> GFCI - Brad, can you elaborate? And if I run it through AC from the
> inverter, is hardwiring the pump a simple, Code-compliant method of
> avoiding
> the GFCI in a damp location (the pump pit)?
>
> Thank you,
> Allan at Positive Energy
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list