Switching Array leads[RE-wrenches]
David Brearley
david at meridiansolar.com
Mon Jul 30 06:22:27 PDT 2007
The system in the HP article uses a transformerless inverter...so both
current carrying conductors are ungrounded.
David C. Brearley
Operations Manager
NABCEP Certified Solar Installer
Meridian Energy Systems, Inc. (TECL: 24461)
2300 S. Lamar Blvd., Ste. 107
Austin, Texas 78704
P: 512-448-0055
F: 512-448-0045
david at meridiansolar.com
www.meridiansolar.com
-----Original Message-----
From: Drake Chamberlin [mailto:Drake.Chamberlin at redwoodalliance.org]
Sent: Saturday, July 28, 2007 4:02 PM
To: RE-wrenches at topica.com
Subject: RE: Switching Array leads[RE-wrenches]
The ungrounded conductors must be switched. In some systems ( I
think under 50 volts) it is still permissible to not have a grounded
circuit conductor, but to switch both. I believe it is code to
break the grounded conductor with a switch, so long as the ungrounded
conductor breaks at the same time.
Drake
At 06:39 AM 7/28/2007, you wrote:
>As I recall, the older code required both the positive and negative
>leads of an array to be switched at the array dis-connect. I think
>at the time there was no DC ground fault required and most of these
>were low voltage arrays. More recently, I believe the code indicates
>only the "un-grounded" lead to be switched, which would imply just
>the positive lead. Since we now have ground fault circuits I think
>this may also be related to the ground fault working properly since
>it needs to "see" the potential between the grounding conductor and
>the negative before it is grounded.
>
>However, in the recent issue of HomePower there is a system showing
>both the positive and negative leads being switched at the array
>dis-connect. Am I wrong and this is not code, ground fault, or high
>voltage related issue and it is up to the installer? Since all
>dis-connects are either 2 or 3 pole, it is not a cost issue, so
>under what (if any) circumstances would you switch only the positive
>and allow the negative and array frame grounding conductor to pass
>through the dis-connect.
>
>Thanks,
>
>Jeff Yago
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list