Galvanic Corrosion yet again [RE-wrenches]
Jim Easton
jeaston at ucsd.edu
Thu Jul 19 22:46:46 PDT 2007
<x-flowed>
I have a feeling we are boring everybody on this list to tears, however I am
not entirely comfortable that your understanding of the situation
corresponds to mine.
When conductive paths are in parallel, the current is shared in inverse
proportion to each path's resistance, and the total potential drop across
each of the paths will be identical.
In other words, when there is a ground loop, connecting a wire between two
grounding electrodes DOES NOT eliminate the potential difference between
them. The various current paths -- including the grounding electrode to
earth to grounding electrode path -- will all share the current and there
will be ground current induced electrolytic corrosion.
If the copper parts of the system are connected to any non-noble (i.e. iron,
steel, zinc, etc.) hardware in contact with the earth, that hardware will be
preferentially attacked and may cause failure of the safety ground.
I like, and Xantrex reccommends, connecting the array ground to the inverter
ground using a bare physically robust (AWG #4 or larger) wire run outside
the conduit in contact with the earth between the PV array and the inverter.
However, the PV neutral should not be connected directly to the array ground
at the array. Connecting a lightning arrestor to the neutral and the hot at
the array to conduct overvoltages to ground is acceptable.
Jim Easton, PE
(E 11974)
4364 Bonita Road, No. 166
Bonita, CA 91902-1421
Tel: 858-527-0240
Fax: 619-470-8616
----- Original Message -----
From: "Bill Brooks" <bill at brooksolar.com>
To: <RE-wrenches at topica.com>
Sent: Thursday, July 19, 2007 7:11 PM
Subject: RE: Galvanic Corrosion [RE-wrenches]
>
> Jim,
>
> I understand the concept of galvanic corrosion and cathodic protection,
> and
> the difference between that and soil corrosion due to soil acidity. I
> think
> your discussion of copper electrodes answers the question. Use copper
> electrodes and this is really not much of an issue and will save a lot of
> copper in the process.
>
> If lightning is an issue, which it is in many places, I will usually bury
> a
> bare copper grounding electrode conductor connecting the two ground rods
> together for maximum protection--no galvanic corrosion because no
> potential
> difference. Also no grounded conductor connection to ground at the array.
> Surge arrestors on all conductors (grounded and not grounded).
>
> Bill.
>
>> -----Original Message-----
>> From: Jim Easton [mailto:jeaston at ucsd.edu]
>> Sent: Thursday, July 19, 2007 8:24 AM
>> To: RE-wrenches at topica.com
>> Subject: Re: Galvanic Corrosion [RE-wrenches]
>>
>>
>> Galvanic (Electrolytic) corrosion caused by DC current flow is different
>> from corrosion caused by soil composition.
>>
>> Galvanic corrosion such as that caused by a DC ground loop will remove
>> metal
>> from the side being corroded in virtually exact proportion to the current
>> flowing and the time it flows.
>>
>> Using copper electrodes can reduce the corrosion since copper has a
>> higher
>> electrochemical potential than hydrogen, and the current will
>> preferentially
>> decompose water rather than corrode the copper. However, any less
>> refractory
>> metal (i.e. iron, steel, zinc, etc.) exposed to the potential will be
>> preferentially corroded leading sometimes to rapid failure. This
>> typically
>> applies to steel bolts, nuts, washers, and cores of copper clad ground
>> rods
>> exposed through abrasion.
>>
>> Jim Easton, PE
>> (E 11974)
>> 4364 Bonita Road, No. 166
>> Bonita, CA 91902-1421
>> Tel: 858-527-0240
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list