form 12-s green tag meter [RE-wrenches]
Todd Cory, Mt. Shasta Energy Services
toddcory at finestplanet.com
Sat Jun 30 08:58:05 PDT 2007
Kelly and others interested in this,
Yes form 12s meters and sockets have 5 terminals.
I am going to do some more testing on this next week, but it appears
only analog meters will work with the Outback directions. If you want to
use a digital meter, it needs to be configured to "net register". This
should be clarified on the Outback green tag metering diagram.
Who is your contact at PSE? I'd like to ask them what kind of "tweaking"
they do to get the digital meters to work correctly.
Todd
Randy Brooks wrote:
>
>
> Todd,
>
> One thing the OutBack diagram does not mention is that the meter base
> requires an additional neutral socket for the 5th meter leg. If you
> meter base does not have one, that may be the problem. You can get a
> 5th socket adapter for your meter base from the meter supplier too.
>
> take care,
>
> Randy Brooks
> Brooks Solar, Inc.
> Solar Power for People
> 140 Columbia View
> Chelan, WA 98816
> 509-682-9646
> info at BrooksSolar.com
> www.BrooksSolar.com
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list