Inverter Output Circuit and DC GEC requirements [RE-wrenches]
Mike Bernhard
spaight12 at sbcglobal.net
Mon Jun 18 16:50:32 PDT 2007
<x-flowed>
Randy,
The answer to your first question is no. Wire, including NM sheathed, must
be protected.
Question Don't think of it as a DC GEC. It is the GEC for the primary side
of the isolation transformer as well as whatever else you would like to call
it Separately derived systems in Art 250. The GEC can be attached to ANY
building grounding electrode including cold water pipe (within 5 ft of where
it comes into the building), building steel, Ufer, ground rod, plate, etc.
Once again, Art 250, separately derived systems.
Mike Bernhard
----- Original Message -----
From: "Randy Hatch" <randy at third-sun.com>
To: <RE-wrenches at topica.com>
Sent: Monday, June 18, 2007 11:01 AM
Subject: Inverter Output Circuit and DC GEC requirements [RE-wrenches]
>
>
> I was hoping that someone could help me to clear up a few items
> that I've been researching.
>
>
>
> 1) Is the inverter output circuit conductor (utility interactive
> inverter) required to be in conduit? NEC reference?
>
> 2) Is the DC GEC required to be run from the inverter to:
>
> a. The DC GE and then bonded to the AC GE (690.47(1))
>
> b. the AC GE (690.47(2))
>
> What should I do for school and commercial installations where providing a
> dedicated DC GEC from the inverter/s to the AC grounding electrode system
> can be considerably more difficult in terms of pathing, distance, etc...
> Is
> there a work-around? NEC reference?
>
>
>
> Thanks.
>
>
>
> Randy Hatch
>
> Third Sun Solar and Wind Power
>
>
>
>
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list