Outback inverter actual ratings [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Sat Apr 28 21:12:19 PDT 2007


Todd,
Now I'm suddenly concerned: We have several Outback PS1 systems in
operation, including one with 3,500 W of PV on the roof. This was checked
out with Outback tech support, as the MX-60 is rated to max 3,200 W of PV.
We haven't been through summer yet with this one: are we in for serious
inverter overheating with this system?

I could sure use some reassurance from C. Freitas about now, after reading
your post.
Allan at PosE

 ----- Original Message ----- 
From: "Todd Cory, Mt. Shasta Energy Services" <toddcory at finestplanet.com>

I just discovered the GVFX3648's continuous at 25º C wattage rating is a
bit... ahhh shall we say "embellished". I recently added more PV to my
home system and now am selling ~2900 watts to the grid. The unit running
with 70º F ambient air was (according to the mate AIR temp readout)
running at 238º F (114º C). According to Outback, the unit was just
about to shutdown from over temperature it was so hot. This is at only
about 80% of the stated load capability!

So I removed the "valve cover", and about half of the bottom plastic
"bug screens" installed in the air exhaust ports. Today the unit was
operating in 88º F ambient temps but was running at 208º F, so assisting
the air flow dropped the internal air temp 30º F with the ambient temp
18º F hotter. This means that improving the air flow greatly improved
the inverters ability to sell at 80% of rated "continuous" loading.

Still running the unit at 208º F does not bode well for the longevity of
the electronics. The next "hack" is to add an air inlet booster fan. If
the internal fan is getting air from an upstream fan the air volume will
be turbocharged. Yes, the ultimate solution is a second inverter, but
why do they sell something that will only make 80% of rated power? I
know this standard practice from the PV manufactures, but I did not know
the inverter manufactures were also doing this. Has anyone else
experienced the rating of other inverters to be a bit more than they
will actually do?

Todd


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list