AC Connection at Fused Disconnect [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Thu Feb 8 08:21:25 PST 2007
Drake,
I assume you read my previous email with the quote from John Wiles.
At the risk of putting myself in an awkward position I am sending another
quote from a personal communication on the subject from John:
"Note the difference between the tap
rules and the requirements for 690.64(B)(2). Feeding a circuit from
both ends (grid and inverter) is not the same as a load circuit with
well controlled power flow."
I personally do not understand Johns concern, nor have I found any
references in the Code that call out the difference that John mentions.
However, I do look to John to speak as an authority on the intent and
direction of the Code.
I really haven't un-raveled the whole thing yet.
Right now the authoritative opinion seems to be that if you mount a fused
disconnect right next to the load center and connect it with a close nipple
and tap it with a conductor that has the same ampacity as the feeder, you
should be in a strong position to argue with an AHJ as to the acceptability.
If you want to mount the fused disconnect ten feet away from the load center
and tap it with a smaller conductor having an ampacity matching the fuses in
the disconnect, you are on your own.
MPF
-----Original Message-----
From: Drake Chamberlin [mailto:Drake.Chamberlin at redwoodalliance.org]
Sent: Thursday, February 08, 2007 7:20 AM
To: RE-wrenches at topica.com
Subject: RE: AC Connection at Fused Disconnect [RE-wrenches]
At 01:24 PM 2/6/2007, you wrote:
>First, the load circuit tap rules in article 240 are superceded by 690.64
>requirements
Having read through 690.64 several times now, I don't see where these
rules supercede the tap rules, or even deal with them in any
way. Where does this interpretation come from?
Drake
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list