208 V 2 pole meter [RE-wrenches]
Steve Johnson
stevejohnson at comcast.net
Tue Dec 11 10:39:40 PST 2007
I have installed a SB 400US in a system with a PV production meter. The
main meter is a 208v, 3 phase CT. The PV production meter is on the
load side of the main meter. From the inverter it goes through an AC
disconnect, through a 2 pole feed through meter base, and onto a 2 pole
breaker in the main panel.
The utility meter guy says his 2 pole 240 v single(split) phase meter
won't read the 208v 2 pole output of the Sunny Boy correctly because it
has a 240 volt coil in it. Says they don't make a 2 pole 208 volt
meter.
Is this right? What to do? I guess I could change the meter out to a 3
phase 208v meter base and they could put in a feed through 3 phase
meter, there just wouldn't be any power on the third leg.
Anybody else run into this?
Steve