SunDanzer Question [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Thu Sep 6 12:35:15 PDT 2007


Wrenches:
We have a longstanding customer with a 24V offgrid home system. He is adding
a Sundanzer 5.8 cubic foot 24V DC chest freezer to his home. We will locate
it in a cool north porch for minimal power consumption. The porch is
directly above a pit containing his 24V Booster Pump and pressure tank, and
I'd like to use the same DC circuit, rather than running new conduit and
wires.

My plan is to use a 24V coil relay in the pump pit. Normally closed contacts
would send power to the freezer, since it has both lower draw and longer
runtime. The pressure switch would activate the relay coil to disconnect
power to the freezer when there is a call for water. It looks like the
freezer draws about 1.6-3.2A, and the pump 8-10A. I don't remember the
conductor size, but it was sufficient for the application when installed.

Anyone tried this? Any problems with this approach? Is it overkill?
Sundanzer specs indicate minimum 22.8 V for the 24V models, but I don't know
if this is a hard number.

Thanks for any responses.

Allan at PosE


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list