Series Parallel PV in Battery systems [RE-wrenches]
David Brearley
david at meridiansolar.com
Tue Nov 21 09:17:53 PST 2006
Damian,
All battery systems require series string fusing regardless of the number of
strings in parallel. The batteries provide a source for fault currents.
The fusing is intended to protect the modules from these potential fault
currents.
David Brearley
NABCEP Certified Solar PV System Installer (TM)
Meridian Energy Systems
2300 S. Lamar, Suite 107
Austin, TX 78704
512-448-0055 (ph)
512-448-0045 (fax)
www.meridiansolar.com
-----Original Message-----
From: Damian de Caires [mailto:damian at thesolarcenter.com]
Sent: Tuesday, November 21, 2006 6:11 AM
To: RE-wrenches at topica.com
Subject: Re: Series Parallel PV in Battery systems [RE-wrenches]
The purpose of fusing is to protect the internal wires of the modules.
If the module is rated for 15amp series, or in some cases like the sharp
167 where it is a 10amp rating. What you need to prevent is in the
event of a short if all the strings minus the one string that the short
would enter into is greater than the amp series max of the module than
you need fusing. A battery system with 2 strings is likely not to need
fusing if the two strings are less than the series rating of the module
(isc x 1.56). Battery systems in general tend to be more likely
candidates because the wiring is high amp at low voltage
-Damian de Caires (Damian at thesolarcenter.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list