Ah, right--and since it's AC there's no way to control direction.
--On Friday, November 03, 2006 10:50 AM -0800 "Todd Cory, Mt. Shasta Energy Services" <toddcory at finestplanet.com> wrote:
>
> Nope, because current flows through this breaker in two directions.
>
> When RE sources are less than the loads, the breaker supplies up to 50 amps of load to a panel to power circuits that will have back up power during grid outages.
>
> When RE sources exceed the loads, backfeeding can supply up to 30 amps to the bus.
>
> Todd
>
>
> Kurt Albershardt wrote:
>
>>
>> Couldn't this be solved with the availability of a 100% rated 30A
>> breaker?
.
- - - -