Hi Ray,

Depends on the type of pump.

2 wire,
3 wire
or no surge Grundfos SQ.

You can run the Grundfos SQ no problem, but also what else is going  
to be running when the pump is on?

jay
peltz power
On Oct 17, 2006, at 1:18 PM, Ray Walters wrote:

>
> Hi Esteemed Wrenches;
>
> I have an existing SW4024 that we are considering using to run a 2  
> hp 240 vac well pump 2000 ft away. We are installing #1 Al for the  
> volt drop, and will run this with a generator for now. I know we're  
> on the line for this mating (my Dankoff info says 1.5 hp with 4kw  
> sinewave, 2 hp with 4.5Kw sinewave inverter). Has anyone run a 2 hp  
> pump (thru a transformer) from a SW4024 or 4048? I've run a 2 hp  
> Pump with a DR3624, but it has a higher surge rating. Just trying  
> to save the customer from buying a 2nd SW4024.
>
> Thanks,
>
> Ray Walters
>


- - - -