Concentric knockouts on circuits over 250 volts [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Sun Aug 27 23:53:51 PDT 2006
Hi
As an electrican I always bond the conduit when
working over 250 volts, even if I run a ground wire in
the conduit. I actually do not know the rule it is
just a habit.
Darryl
--- "Bob-O Schultze, Electron Connection"
<econnect at snowcrest.net> wrote:
>
> William,
> If I read this right, this only applies to
> situations where one is
> using the EMT or the like as the grounding
> conductor. Where one
> carries a grounding conductor from the PVs down to
> the DC disco and
> it is bonded to all the metal boxes using a lay-in
> lug or the like, I
> don't see the need for the bonding bushings. Just my
> thoughts, I
> could be wrong.
> Bob-O
> On Aug 27, 2006, at 12:18 PM, William Miller wrote:
>
> >
> > Friends:
> >
> > It has come to my attention that bonding bushings
> are required in
> > our DC feeder conduit where it enters the DC
> disconnect via
> > concentric knockouts per NEC:
> >
> > 250.97 Bonding for Over 250 Volts.
> > For circuits of over 250 volts to ground, the
> electrical continuity
> > of metal raceways and cables with metal sheaths
> that contain any
> > conductor other than service conductors shall be
> ensured by one or
> > more of the methods specified for services in
> 250.92(B), except for
> > (1).
> > Exception: Where oversized, concentric, or
> eccentric knockouts are
> > not encountered, or where a box or enclosure with
> concentric or
> > eccentric knockouts is listed for the purpose, the
> following
> > methods shall be permitted:
> > (a) Threadless couplings and connectors for cables
> with metal sheaths
> > (b) Two locknuts, on rigid metal conduit or
> intermediate metal
> > conduit, one inside and one outside of boxes and
> cabinets
> > (c) Fittings with shoulders that seat firmly
> against the box or
> > cabinet, such as electrical metallic tubing
> connectors, flexible
> > metal conduit connectors, and cable connectors,
> with one locknut on
> > the inside of boxes and cabinets
> > (d) Listed fittings that are identified for the
> purpose
> >
> >
> > 250.92 Services.
> > (B) Method of Bonding at the Service. Electrical
> continuity at
> > service equipment, service raceways, and service
> conductor
> > enclosures shall be ensured by one of the
> following methods:
> > (1) Bonding equipment to the grounded service
> conductor in a manner
> > provided in 250.8
> > (2) Connections utilizing threaded couplings or
> threaded bosses on
> > enclosures where made up wrenchtight
> > (3) Threadless couplings and connectors where made
> up tight for
> > metal raceways and metal-clad cables
> > (4) Other approved devices, such as bonding-type
> locknuts and bushings
> > Bonding jumpers meeting the other requirements of
> this article
> > shall be used around concentric or eccentric
> knockouts that are
> > punched or otherwise formed so as to impair the
> electrical
> > connection to ground. Standard locknuts or
> bushings shall not be
> > the sole means for the bonding required by this
> section.
> >
> >
> >
> > William Miller
> >
> >
> >
>
__________________________________________________________________
> > William Miller
> > Miller Power and Communications
> > Voice :805-438-5600 Fax: 805-438-4607
> > email: wrmiller at mpandc.com
> > http://mpandc.com
> > License No. C-10-773985
> >
>
_____________________________________________________________
> > Check out our latest project at
> http://mpandc.com/case_studies/
> > pv_school/pv_school.html
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages:
> http://lists.topica.com/lists/RE-
> > wrenches/read
> >
> > List rules & how to change your email address:
> www.mrsharkey.com/
> > wrenches/etiquette.php
> >
> > Check out participant bios:
> www.mrsharkey.com/wrenches/
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list