3-phase generator [RE-wrenches]
Bob Ellison
ellison at gisco.net
Tue Jun 13 23:06:33 PDT 2006
If the generator is a 12 wire reconnectable it can be rewired to single
phase but here is the problem, (one of many) you generally loose 40% of the
output when you reconfigure it. Take 40% off a 5 K generator and there is
not much left!
I agree with Christopher, find and old motor guy for the best advice.
Bob
-----Original Message-----
From: Christopher Freitas --- OutBack Power
[mailto:cfreitas at outbackpower.com]
Sent: Tuesday, June 13, 2006 1:38 PM
To: RE-wrenches at topica.com
Subject: RE: 3-phase generator [RE-wrenches]
Many three phase generators can be configured for single or three phase
output by reconnecting the windings of the generator. I doubt that this
would be something covered in the manual though. You might check around for
a motor rewinder guy (the older the better from my experience) and see what
he says. You probably will need to put in a bigger single pole breaker (on
some they just parallel the three poles together which is
marginal).
There is no three phase to single phase balancing transformer solution that
I am aware of.
If he is going to run large a large 3 phase load (such as a pump) along with
the single inverter on one phase - then its OK.
If the only load is the inverter - be careful to limit the draw to about
1/3 of the generator's rating or you can overload a winding (which there is
no temperature sensing to protect).
Christopher
Nicholas Ponzio wrote:
>
> We've got a possible off-grid client that already owns a 3-phase
> generator (5kVA Onan). He only needs a single inverter. Any clean way
> to do this?
> 3-to-1 balancing x-former? If not, how bad is it for the generator to
> only use a single leg?
>
> Thanks for any input.
> -Nik
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list