3-phase generator  [RE-wrenches]
    Christopher Freitas --- OutBack Power 
    cfreitas at outbackpower.com
       
    Tue Jun 13 10:38:17 PDT 2006
    
    
  
Many three phase generators can be configured for single or three phase 
output by reconnecting the windings of the generator.  I doubt that this 
would be something covered in the manual though.  You might check around 
for a motor rewinder guy (the older the better from my experience) and 
see what he says. You probably will need to put in a bigger single pole 
breaker (on some they just parallel the three poles together which is 
marginal).   
There is no three phase to single phase balancing transformer solution 
that I am aware of.  
If he is going to run large a large 3 phase load (such as a pump) along 
with the single inverter on one phase - then its OK.  
If the only load is the inverter - be careful to limit the draw to about 
1/3 of the generator's rating or you can overload a winding (which there 
is no temperature sensing to protect).  
Christopher
Nicholas Ponzio wrote:
> 
> We've got a possible off-grid client that already owns a 3-phase 
> generator
> (5kVA Onan). He only needs a single inverter. Any clean way to do this?
> 3-to-1 balancing x-former? If not, how bad is it for the generator to 
> only
> use a single leg?
> 
> Thanks for any input.
> -Nik
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
    
    
More information about the RE-wrenches
mailing list