Jeff,
We've had good luck with the smaller Concorde AGM (105 Ah SunXtender)
in Chihuahua. We have a couple hundred SHS installations with them
working 6.5 years now (~15% DOD). For hot areas (e.g., East Africa), I
think AGM would probably be a better long-term choice than gel.
We've used the industrial class Absolyte in schools in Central America
with good results for the past 5 years.
I'd be interested to hear more about your work (off-line) in East
Africa as we are planning projects in Sudan and Kenya.
Robert Foster
On May 19, 2006, at 1:13 PM, Jeff Lahl wrote:
>
> Hi Wrenches,
> Have recently rejoined the group after a long absence so please
> excuse if this is an old, already-covered topic.
>
> We're going to need sealed batteries for several dozen rural health
> centers in East Africa and are trying to figure out the best to use.
> Up to now, we've mostly used standard wet batteries so we're on a
> learning curve here. My reading seems to indicate that AGM is more
> state-of-the art than gel but I am getting conflicting reports on
> specific products: for instance in the 12v 250ah class, I'm hearing
> that the Deka gel has better cycling life than the Concorde AGM.
> Anyone have alot of experience with either, and especially with
> comparing the two? What kind of life are you seeing under what DOD?
>
> In a heavier, industrial class, does anyone have favorite sealed
> batteries? I'm aware of Unigy and Absolyte - are there any others to
> consider?
>
> Finally, I'm more than a little concerned about a charge controller
> failure resulting in overcharging and ruining these $4,000 battery
> banks in remote locations. Has anyone tried integrating a
> voltage-tripped relay that would open the charging circuit - as a kind
> of fail-safe mechanism?
>
> Will appreciate input on any of the above.
> Thanks much,
> Jeff Lahl
> Project Director, Solar Electric Light Fund
>
>
>
> --
> [Non-text portions of this message have been removed]
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list