The type of current flow, (AC or DC) has nothing to do with the 
direction of current flow.  You control direction by how much you are 
producing and how much you are consuming.  Supply and demand.  

Kurt Albershardt wrote:
> 
> Ah, right--and since it's AC there's no way to control direction.
> 
> 
> 
> 
> --On Friday, November 03, 2006 10:50 AM -0800 "Todd Cory, Mt. Shasta 
> Energy Services" <toddcory at finestplanet.com> wrote:
> 
> >
> > Nope, because current flows through this breaker in two directions.
> >
> > When RE sources are less than the loads, the breaker supplies up to 50 
> > amps of load to a panel to power circuits that will have back up power 
> > during grid outages.
> >
> > When RE sources exceed the loads, backfeeding can supply up to 30 amps 
> > to the bus.
> >
> > Todd
> >
> >
> > Kurt Albershardt wrote:
> >
> >>
> >> Couldn't this be solved with the availability of a 100% rated 30A
> >> breaker?
> 
> 
> 
> 
> 
> 
> 
> .


- - - -