Minor correction here with large consequences to the question at hand...a
C/5 rate is "capacity at a five-hour rate", or 20% of the battery's amp-hour
rating, rather than 5%.
Allan at Pos Energy
----- Original Message -----
From: "Ezra Auerbach, DragonSun Consulting" <ezra at lasqueti.net>
>
> I totally agree with Drake, your next challenge will be charging
> those batteries. You need an on-site ability to apply C5 (5% of the
> battery banks amp hour rating at the 20 hour rate).
- - - -