Kaneka GSA? [RE-wrenches]
Bill Brooks
bill at brooksolar.com
Wed Aug 16 14:04:26 PDT 2006
So Matt,
What would the appropriate fuse rating be for two series strings in
parallel?
Assuming the Isc is 1 amp, then Imax = 1 amp x 1.25 = 1.25 amp [690.8(A)].
Therefore you must subtract the 1.25 amps from the 5 amp rating so the max
fuse rating is 3.75 amps
Two strings in parallel have a max current of 2.5 amps (1.25 x 2), and the
minimum series fuse rating is 2.5 amps x 1.25 = 3.1 amps [690.8(B)]. So the
correct number is 3.5 amps.
The only fuse allowable for this arrangement of two strings in parallel is a
3.5 amp fuse. I'd be interested to see if they have this in their
literature.
Bill.
-----Original Message-----
From: Matt Tritt [mailto:solarone at charter.net]
Sent: Tuesday, August 15, 2006 8:55 AM
To: RE-wrenches at topica.com
Cc: Travis Creswell, Ozark Solar
Subject: Re: Kaneka GSA? [RE-wrenches]
-Hi Travis,
The panel label info. trumps the manual info, so that would be 5 amps. The
actual output from a series string is about 1 amp and they are designed to
be fused for 2 parallel strings with a single fuse.
Matt T
DC Power Systems
--- "Travis Creswell wrote:
>
> Can someone tell me what the "series fuse" rating of the Kaneka 60
> watt module is?
>
> Any comments on this module would be welcome.
>
> Thanks in advance,
>
> Travis Creswell
> Ozark Energy Services
> www.ozarkenergyservices.com
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list