Hi David,
The AGS mode in the mate has lots of parameters including quiet time.
( if you have an old mate they don't have the AGS mode)
You will only need a 12v relay as the contacts from the FX are 12
powered, but the Kohler is ground started. So just connect the relay
to close on command from the aux relay and hook up the NO contacts to
the genny and you are set to go.
jay
peltz power
On May 12, 2006, at 5:48 AM, David Palumbo, Independent Power & Light
wrote:
>
>
> What part(s) do I need to add to a basic Out Back off grid pv
> system for
> automatic gen start/stop? Must include a clock prohibiting gen run
> during
> overnight (the old Trace SW quiet time).
>
> Client just received a brand new two wire start Kohler LP 8.5k
> (8.5RES)generator. As far as I can see the OB FX2524T and Mate do
> not have a
> quiet time in their program.
>
> Would any of the after market gen control products help with this?
> Such as
> Solar Converters GS2, or GSCM's control module?
>
> Thanks for your help,
>
> Dave
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list