HI Kirk
I have done two such and it looks like I might do a
third. In both my cases the generators are small, 1.8
to 2.2 kW, the third one I might do is also small,
less than 3 kW for sure, perhaps a 2 kW. ( the owner
has not purchased as yet) In my case it is just for
emergency recharge of the battery set.  One battery
set is 48 volt 1200 AH and the second is 48 volt 400
AH.  The third one will be a 48 volt string of L16s
(about 400 AH). 

I have used the Outback X240 and put the 120 volt
generator into the 240 volt side and taken 60 volts
out of the 120 volt side.  So I did not use a
isolation transformer.  (Chris used an isolation
transformer)

I have had no problems with either setup.  I set the
max MX 60 charge rate to limit the generator current
to values the generator can handle.  The 2.2 kW is set
up with a 1.2 kW PV array in parallel with the
generator-transformer-rectifier circuit.  I placed a
rectifier in series with the PV array also, but I am
not sure that I needed to.  I had to set the MX limit
for the generator to about 1.8-1.6 kW (I do not
remember the exact amount).  The generator seemed as
if it could not handle full rating.  Also the MX 60 at
times seemed to squel slightly ( a high pitch maybe
3000 hz).  Both systems have functioned as expected. 
If perchance the generator and the PV were to operate
at the same time the load on the generator would be
reduced.
Darryl

--- Kirk Herander <kirk at vtsolar.com> wrote:

> Your free subscription is supported by today's
> sponsor:
>
-------------------------------------------------------------------
> Is your computer freezing up or slowing down?
> Repair corrupt files and harmful errors - protect
> your PC
> Take a 2-minute PC health check-up at no charge!
> http://click.topica.com/caaeE3vbz8Qcsbd5Ekwa/PC
> Powerscan
>
-------------------------------------------------------------------
> 
> Chris F.,
> 
> You mentioned that the MX60 could be used for both
> PV and generator
> charging. I'm wondering if the output of the
> rectifier can be paralleled
> with the PV inputs without causing harm - due to
> overloading the MX60 or
> just in general - or if some switching is necessary
> to isolate the array
> when the generator is charging through the
> transformer/rectifier/mx60.
> 
> And I assume generator charging through the MX60
> voids its warranty,
> right?
> 
> Kirk Herander
> Vermont Solar Engineering
> 802.863.1202
> fax 802.863-7908
> NABCEP(tm) Certified Solar PV Installer
> Xantrex Certified Dealer Charter Member
> NYSERDA-eligible installer
> VT Solar and Wind Partner
> 
> 
> 
> "We have also played around with the MX60 and a
> isolation transformer 
> with rectifier - and it does work pretty well - just
> keep in mind that 
> its limited to around 800 watts at 12vdc, 1600W at
> 24vdc and 3200W at 48
> 
> vdc.  
> 
> You can also use the same MX60 controller for the PV
> array if the 
> back-up generator is only used at night or during
> poor weather 
> conditions (which is almost always the case).  
> 
> This solves a couple of problems - such as poor
> quality generator 
> waveform and the grounded-neutral of nearly all
> portable generators.
> 
> Using the MX60 allows the charging process to be
> coordinated with the 
> rest of the system - such as EQ and temp
> compensation control.  You also
> 
> get the metering functions as well displayed on the
> MATE.  
> 
> You will not find a charger which offers three stage
> charging and 
> metering for anywhere near the price of a MX60 and a
> isolation 
> transformer."    
> 
> 
> 
> -- 
> ----------------------------------------
> I am using the free version of SPAMfighter for
> private users.
> It has removed 12539 spam emails to date.
> Paying users do not have this message in their
> emails.
> Try www.SPAMfighter.com for free now!
> 
> Your free subscription is supported by today's
> sponsor:
>
-------------------------------------------------------------------
> See the hottest games before your friends! Sign up
> with Ubisoft, 
> and you'll get access to exclusive game news,
> contests, promotions, 
> community forums, and more. It's easy, free, and
> secure.
> http://click.topica.com/caaeInYbz8Qcsbd5Ekwf/
> Ubisoft
>
-------------------------------------------------------------------
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
>
> 
> 
> 


__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com 



More information about the RE-wrenches mailing list