Thanks Kent
I take it the AC2 of the Outback provides the sync
signal to the windyboy.  But when the outback needs to
charge the battery it needs to be connect to AC1
correct?  I seem to be missing something? 

Is one outback connected AC2 and the other connected
AC1?  

Thanks but the inverter generator does not follow the
sync signal of the outback (I don't think)?.

Thanks your project is very interesting.
Darryl  

--- Kent Osterberg <kent at coveoregon.com> wrote:

> Darryl
> 
> I've got a off-grid customer with a Windyboy that we
> recently set up in 
> parallel with and Outback tri-stack.   Didn't do
> this without 
> information from Outback that it work.  The Windyboy
> is connected to the 
> ac output bus and the FX inverters charge the
> batteries, negative output 
> current form the FX's, to provide ac voltage
> regulation.  The Mate shows 
> zero kW in and zero kW out, but the Trimetric shows
> positive battery 
> current.  The FX's normal battery charging controls
> and settings do not 
> work, it'll charge the batteries until there is a
> high voltage 
> disconnect.  You'll want to use the aux output to
> shut down the parallel 
> source before that happens.
> 
> Kent Osterberg
> Blue Mountain Energy, LLC
> 