Friends:
I had just asked the question referred to below and received your gracious
answers when I was called out today to look at installation of a 30KW
residential system. This translates to over 100 AAC. The meter main is a
CH HP404040SHA,
(http://www.ch.cutler-hammer.com/unsecure/cms1/TB00500001E.PDF page 73) a
400 amp meter main combo with two 200 A main breakers. One feeds a 200 A
buss and one feeds a remote sub panel.
There is no combination that allows me to feed 125 A into the 200 A
buss. The inverter current, rated up for continuous duty is 170.45 (at 220
VAC). The buss rating times 1.2 is 240. This allows me a 70 A breaker
which won't even handle the PV generation current.
I'm not sure I can tap the conductors between the meter socket and the buss
bars, they are very short, bent into a curve and they are part of a listed
assembly.
Wait, I think I just now got the answer! There will be a 200 A feeder from
the second main to a sub-panel. How about if I tap the conductors going to
the sub? This way I'm not feeding a buss and I don't have to tap between
the meter and the buss. Any comments?
William Miller
At 09:09 AM 1/20/2006, you wrote:
>William,
>To clarify... we connect after the main disconnect, using a back-fed
>breaker and folowing the 120% rule, whenever possible. But sometimes you
>just have to connect ahead of the main breaker. In that case, you can use
>a Polaris connector, or a split bolt if you really wrap it well with
>electrical tape and 3M tape, or a technique we use often is to find an
>existing 10-32 or 1/4-20 stud on the buss bar which feeds the main
>breaker, and use a standard wiring lug to attach your #8, #6, etc wires
>which go to your fused disconnect. Obviously make sure everything is
>tight and properly torqued down and there is no possibility of the lug or
>connector shorting to the case. We do not connect at the bottom of the
>meter because the utility guys get upset at this. Finally, we have never
>drilled and tapped the buss bar, but that seems to be a reasonable
>last-ditch option as long as the precautions above are followed. Put
>anti-oxidant paste over the junction of the aluminum lug and the copper
>buss bar. And be careful if you are working on it hot!
>
>Mark
>Cobalt Power Systems, Inc.
--
[Non-text portions of this message have been removed]
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Jumpstart your love life at AmericanSinglesR.com.
Meet someone in your area today. Millions of member profiles.
Create a profile, post photos and search for free.
http://click.topica.com/caaemrrbz8Qcsbz9JC9f/Spark Network
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list