Help w/large o-t-g inverter! [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Tue Jun 21 21:23:22 PDT 2005
Hello
I have a motor with 130 amps starting surge on the
grid, and I start this load with 4 outback VFX3648s.
I do not know the starting current with the outbacks
but I think it must be less. The outback might sort
of soft start the motor.
Please note that not all motors are the same. B type
induction motors start withcurrent and less torque
than say D type. Submersible pumps have a higher
starting surge per hp than other motors. Also
submersible motors have a bearing than must be
presurized very soon after start and therefore do not
like to be soft started.
Darryl
--- Ray Walters <ray at solarray.com> wrote:
> I've got 2 Outback related questions while were at:
> 1) Can you stack three inverters with a transformer
> for 3 wire single phase
> 220? ( a customer wanted to save some money)
> 2) What is the maximum pump HP that can be run with
> a pair of Outback VFX
> 3648s. I have two customers each with deep well 3 Hp
> submersibles.
> My Franklin motor book shows for a 3 HP pump a
> maximum current of 17Amps
> (230v) but a locked rotor current of 83 amps,
> meanwhile their suggested
> breaker size is 40 amps. The Outback 1Ms surge is 70
> amps, the 100Ms surge
> is 50 amps, the 5 sec surge is 41.6 amps. Sure seems
> like a pair of the
> Outbacks would run a 3 Hp pump, but could overload
> occasionally with other
> loads on.
> I've run a 2 Hp pump with a single DR 3624 and T240
> transformer, although I
> advised the customer to use it for emergencies only.
> Any real experience with Outbacks out there?
>
> Thanks beforehand,
>
> Ray Walters