Kurt,

There are two types of grounding conductors: (1)equipment grounding
conductors; and, (2) grounding electrode conductors. I assume you are asking
about the latter.

250.166 says that it shall be no smaller than 8AWG, but it also says that it
shall be no larger than... and then goes into details about ground rods,
concrete encased, and ground grids. Short answer is that normally it will
not be greater than 4AWG unless you have a ground grid.

Bill.


-----Original Message-----
From: Kurt Nelson [mailto:sunwise at cheqnet.net] 
Sent: Friday, March 18, 2005 1:46 PM
To: RE-wrenches at topica.com
Subject: Grounding conductor [RE-wrenches]

Greetings all,

I remember years ago we were told that the grounding electrode conductor had
to be as large as the largest conductor in the system, often a 2/0 or 4/0
cable (nobody did it).  I thought in the last writing of the NEC (or the one
before that) a provision was made allowing for a more reasonable sized
grounding electrode conductor.

Yet for the life of me, I can't seem to find it.  690 says to use 250.166
and (B) (weren't not talking A) says the grounding electrode conductor shall
not be smaller than the largest conductor supplying the system and not
smaller than 8 AWG copper, etc.

Are we still supposed to be compliant with this code or is there something
here I am not seeing?

Thanks in advance -- Kurt Nelson

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without painful injections with Nexiderm SP.
Nexiderm SP is clinically proven to reduce wrinkles by 68% Start 
your free 14-day trial today!
http://click.topica.com/caadfBPbz8Qcsbz9JC9f/Nexiderm
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list