Grounding conductor [RE-wrenches]
Kurt Nelson
sunwise at cheqnet.net
Fri Mar 18 13:46:08 PST 2005
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Want a laptop? Get an Apple iBook for free!
http://click.topica.com/caadeMmbz8Qcsbz9JC9a/Amazing Computer
-------------------------------------------------------------------
Greetings all,
I remember years ago we were told that the grounding electrode conductor
had to be as large as the largest conductor in the system, often a 2/0
or 4/0 cable (nobody did it). I thought in the last writing of the NEC
(or the one before that) a provision was made allowing for a more
reasonable sized grounding electrode conductor.
Yet for the life of me, I can't seem to find it. 690 says to use
250.166 and (B) (weren't not talking A) says the grounding electrode
conductor shall not be smaller than the largest conductor supplying the
system and not smaller than 8 AWG copper, etc.
Are we still supposed to be compliant with this code or is there
something here I am not seeing?
Thanks in advance -- Kurt Nelson
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
How would you like a Complimentary Kmart $500 GiftCard by
participating in our special promotion?
http://click.topica.com/caadi1cbz8Qcsbz9JC9f/RewardsVenue
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list