Hey Todd and Travis,
Another way to solve this problem might be to replace the pump with
something a little easier to handle, maybe like a Grundfos SQ or SQE
with variable speed/constant pressure. This way you can avoid the
(absolutely necessary) storage tank and added pressure pump costs, not
the least of which will be the labor. I don't know how they would work
with the squarewave, but it wouldn't hurt to ask Grundfos about it.
Matt T
Travis Creswell, Ozark Solar wrote:
>Hello Todd,
>
>I'm kind of surprised they won't start it.
>
>What's the starting and running amps? This is a three wire pump, right? It
>should say right on the box what the starting and running amps is supposed
>to be. What's the battery bank dipping down to? A few bad batteries could
>really pull the bank down. I've seen that several times. And see if you
>can't talk them into eliminating a few of those parallel strings.
>
>Are the battery cables already 4/0? When it's close to working, the
>shortest and largest battery cables possible can really help with surge
>problems. I did a lot of playing around with this one time to get too small
>of an inverter to start an AC unit for an RV.
>
>What's the pressure switch set at? If it's a 40/60 you might solve the
>problem most of the time by changing out to a 20/40.
>
>What about using the 240v well pump to fill atmospheric storage tank? Then
>using a small pump (12 volt DC?) for pressure? You could prove if this
>would work by testing to see how reliably the pump would start when the
>pressure is 0 psi. Turn the well breaker off - then open a tap until the
>water stops running - turn the breaker back on, etc.
>
>Good Luck,
>
>Travis Creswell
>
>-----------------
>From: Todd Cory, Mt. Shasta Energy Services toddcory at finestplanet.com
>Date: Sun, 07 Aug 2005 08:55:45 -0700
>To: RE-wrenches at topica.com
>Subject: 1.5 HP well pump [RE-wrenches]
>
>Wrenches,
>
>I inherited a poorly designed off grid system I am working on. It has a
>stacked (240 volt) pair of DR1512 inverters fed by 12 L-16H batteries
>(12 volts at 2500 a/h!!) trying to start a 1.5 HP well pump! The
>inverters amazingly can occasionally start the pump when the batteries
>are fully charged, but you know this has got to be a struggle for them.
>
>I recall at one time someone saying increasing the capacitance of the
>starting capacitor would ease the starting. It has a 240 volt 120 MFD
>one now. What would people suggest (other than larger inverters) to make
>this pump start reliably? Doesn't someone make a soft start control for
>a well pump?
>
>Thanks,
>
>Todd
>
>
>
>
>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Hershey’s® or Ghirardelli® Chocolate?
Take our Nationwide Chocolate Survey today!
Receive a FREE* $100 restaurant gift card of your choice or $100
worth Hershey’s® or Ghirardelli® Chocolate for participating!
http://click.topica.com/caadOv3bz8Qcsbz9JC9f/Chocolate Survey
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list