SW4024 with control problems [RE-wrenches]
Matt Tritt
solarone at charter.net
Tue Jul 5 20:13:37 PDT 2005
<x-flowed>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get a Free Sirius Satellite Package, don't pass on this!
http://click.topica.com/caadHlCbz8Qcsbz9JC9a/ProductTestPanel
-------------------------------------------------------------------
Drake,
Wow; is this de ja vu, or what? I just got back from an off-grid install
I put in a number of years ago with very similar symptoms. In this case,
however, I think I've traced all the problems back to a 4/0 cable
connection (-) that managed to loosen-up over about 4 years. It wasn't
so difficult to find the problem, seeing as how the DC bonding block got
hot enough to fry some of the insulation off a controller lead connected
to the same block. =(:-0 !!
The report from the owners (who never seem to check anything until it
breaks) was that: in auto mode the generator would run for hours, stop
for about 15 minutes, then run for hours, ad nauseum. Even with the
genny going full-tilt the bad connection prevented a full charge from
ever being accomplished (for very long). I am not a big fan of the
bonding block arrangement in the Trace DC box for several reasons, not
the least of which is it's deep location - way to one side, which can be
a hassle in some installations.
So, even if your problem is not the negative connection, I suggest
re-torquing all the connections within the DC enclosure to original
spec's as a preventative measure. But you probably already did that!
Matt T
Drake Chamberlin wrote:
> Your free subscription is supported by today's sponsor:
> -------------------------------------------------------------------
> Need Emergency Cash? Get Up To $500 Now! No Credit Checks, Easy & Fast
> Approval Cash in you account Overnight!
> http://click.topica.com/caadHk3bz8QcsbadqCja/911PaydayAdvance
> -------------------------------------------------------------------
>
> Hi Wrenches,
>
> I'm working on an SW4024 that is being used in as a grid back up, that
> exhibited two strange malfunctions while on the wall.
>
> 1) It would take several seconds to come on after the grid was shut off.
>
> 2) Whenever the generator was in the AUTO mode, it would run the
> generator. OFF turned the generator off, but AUTO works the same as
> ON. The battery bank is full and the generator goes on even with very
> small loads, so it doesn't appear to be a load start issue.
>
> After cold starting the inverter, it would work normally for a short
> time, then revert to its strange behavior.
>
> Now the inverter is in the shop, but they can't find anything wrong
> with it. Does anyone have any idea what is going on?
>
> Thanks,
>
> Drake
>
> Your free subscription is supported by today's sponsor:
> -------------------------------------------------------------------
> Get up to $1500.00 Fast and Easy!
> No Credit Checks! No Paper Hassles! Nothing To Fax!
> Apply Online and We'll Contact You Within the Hour!
> http://click.topica.com/caadHk7bz8QcsbadqCjf/911PaydayAdvance
> -------------------------------------------------------------------
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Need a Laptop? Get a Sony Vaio Laptop Free!
http://click.topica.com/caadHlxbz8Qcsbz9JC9f/ProductTestPanel
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list